GFI plugged in to a GFI

Status
Not open for further replies.

mudcat555

Member
Location
Mentor, Ohio (25 miles east of Cleveland)
Occupation
Retired Electrician IBEW Local 38
This is the situation. Customer bought exterior sidewalk heating mats. The mats come with a weatherproof GFI built right in to the male cord end. The outside receptacle that they want to plug in to is also a GFI . Can a GFI be fed by a GFI without causing any undesirable effects and nuisance tripping?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
There is an exception to 210.8. I wonder if the cord has gfci or gfpe. My guess is it is gfpe

(3) Outdoors
Exception to (3): Receptacles that are not readily accessible and are
supplied by a branch circuit dedicated to electric snow-melting, deicing,
or pipeline and vessel heating equipment shall be permitted to be installed
in accordance with 426.28 or 427.22, as applicable.
 

kwired

Electron manager
Location
NE Nebraska
Leakage detector is basically same thing as GFPE and very possible that any minor leakage will trip GFCI but not the leakage detector simply because of lower trip threshold of the GFCI.

Any situation where there is enough fault current to trip both will mean you must reset both, but having both doesn't create any interference of any kind between them.
 

GeorgeB

ElectroHydraulics engineer (retired)
Location
Greenville SC
Occupation
Retired
Can a GFI be fed by a GFI without causing any undesirable effects and nuisance tripping?
When I hooked my test equipment (3 120VAC devices) at a customers' pants, I used a GFCI triple outlet short cable. This is one of those that has to be reset every time power is lost (is unplugged). I never tripped the GFCI many plants had on the production floor.
 