GFI protection of imersion heaters and pumps

Status
Not open for further replies.

blacklog

Member
One of the areas in my manufacturing plant is plating (of metal strip). One or our contractors contends we need GFI protection of our hard wired imersion heaters (we also have hardwire pumps, etc.) Many other vendors do not agree this is required, although the heater manufacturer recommends it - for liability? I personally know of a lot of hardwired equipment in 'wet' environments that is not GFI protected. For example we have electric heat in thermalators in molding (They keep the molds at a certain temp) and they are not 'GFI'd'. Allowing this could mean a retrofit of our entire shop. Can anyone point out code support for either view?
 

blacklog

Member
Re: GFI protection of imersion heaters and pumps

I believe I have resolved this issue but still would appreciate a nod of approval or further adivce from someone who knows more than I do. 427 covers fixed electric heat. 427-22 requires Ground Fault protection of electric heat tracing and heating panels only. Earlier editions required ground fault protection for electric heating equipment without metal coverings.
 