My question is in a plant application. Do the counter tops in a chemical lab require ground fault protection?
 
Is it required? Nope. Reference: NEC article 210.8(B).

Is it a good idea anyway? I think so.

Welcome to the forum.
 
JHARPER,

The answer is maybe. The 2008 NEC would require GFCI protection within 6' of a sink in 210.8(B)(5) although exception 1 to 210.8(B)(5) might get you right back out of the requirement:). All of this, of course, is dependent on whether or not a sink is installed in that countertop.

BTW, welcome to the forum!