Does the Code require GFCI protection on a heater circuit for an open industrial tank with a 208V/1ph encased heater? The 120V control panel is GFCI protected as there are receptacles for auxiliary equipment for the process and the heater circuit runs through the control panel via a contactor for temperature control. The 4K heater circuit causes the 2-pole/20A GFCI breaker to trip due to initial resistance of 150K ohms to ground. This resistance to ground increases to 20M+ ohms as the heater operates and removes internal moisture due to humidity, which will then allow the GFCI CB to reset. Any thoughts??