GFI Questions

Status
Not open for further replies.

S'mise

Senior Member
Location
Michigan
Reading another post on gfci's sparked a few questions in my mind.

Why do gfci receptacles trip (need to be reset) whenever you loose power?
Are all receptacle type gfci's designed like that?

Why cant they be like the gfci cord on the end of a hair dryer? (dont have to be reset every time you plug them in?)

There are times that the latter would sure be handy, instead of using a gfci breaker.
 

rcwilson

Senior Member
Location
Redmond, WA
None of my GFCI receptacles trip when I loose power. I have a lot around the house, garage and driveway.

I haven't heard of any of the ones at the plant's we build tripping on power outages, and there has been a lot of plant outages.

Maybe something is happening in your system to cause them to trip.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I believe there was a vintage of male receptacle cord ends that would trip when the power went off. It is a safety think in shops and other areas where machines needed GFCI protection but you didn't want a table saw coming on when the power came back on.

I had one that was made for the construction site to protect workers from getting hurt. I believe there still are some out there.
 

Twoskinsoneman

Senior Member
Location
West Virginia, USA NEC: 2020
Occupation
Facility Senior Electrician
Reading another post on gfci's sparked a few questions in my mind.

Why do gfci receptacles trip (need to be reset) whenever you loose power?
Are all receptacle type gfci's designed like that?

Why cant they be like the gfci cord on the end of a hair dryer? (dont have to be reset every time you plug them in?)

There are times that the latter would sure be handy, instead of using a gfci breaker.

If GFCIs did that these days that would be a deal breaker for me. There would be at least a couple coming out of my work shop.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
All of the older "portable" GFCIs did that, but I have never run across a GFCI intended for fixed use that did that. Portable GFCIs require "open neutral protection" and with the older ones they used a relay on the line side of the GFCI sensor to provide the open neutral protection. You had to push the reset each time the device was powered up to pull the relay in.
 

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
All of the older "portable" GFCIs did that, but I have never run across a GFCI intended for fixed use that did that. Portable GFCIs require "open neutral protection" and with the older ones they used a relay on the line side of the GFCI sensor to provide the open neutral protection. You had to push the reset each time the device was powered up to pull the relay in.


I've only seen that on portable cords and GFCI's. I have some myself.
I have seen homes hit by utility faults where the GFCI's were tripped.
 

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
There has been a change in the UL standards for GFCI receptacles, where now they are required to have 'miswire' protection. These GFCI's can't be reset unless there is power supplied to the line terminals, and not the load terminals. Some of the designs to incorporate this protection include tripping whenever the power is interrupted.

http://tools.passandseymour.com/ProductKnowledge/course.cfm?course_sak=25&cur_page=0&cur_seq=0

That is one reason that i refuse to use them on my jobs.... I love them at other peoples jobs though. :D
 