GFI receptacle readily accessible in Baltimore?

Status
Not open for further replies.

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
Just looked at a job where the inspector required gfi breakers instead of allowing receptacles because he considered moving a countertop microwave to reset the receptacle “not readily accessible” Guess the job is too close to DC! LOL! Talk about taking it too far!
 

K8MHZ

Senior Member
Location
Michigan. It's a beautiful peninsula, I've looked
Occupation
Electrician
Just looked at a job where the inspector required gfi breakers instead of allowing receptacles because he considered moving a countertop microwave to reset the receptacle “not readily accessible” Guess the job is too close to DC! LOL! Talk about taking it too far!
Going by the NEC definition, I agree with the inspector. Moving a microwave is moving an obstacle.
 

retirede

Senior Member
Location
Illinois
How often are countertop appliances present during final?
Never in the case of new construction, rarely for remodels.
Or does the inspector just pick a spot and decide that’s where the microwave will be placed?
 

Rock86

Senior Member
Location
new york
Occupation
Electrical Engineer / Electrician
Hmm... I'm curious. If it is a counter top receptacle, then no kitchen could pass inspection based on the above thought. You could have a toaster oven or mixing machine in the way of a GFCI receptacle just as easily as a microwave. Unless of course the microwave is fastened in place, I'm not sure I agree with the inspector. Could the microwave be kicked off the side far enough to expose the receptacle in question?
 

synchro

Senior Member
Location
Chicago, IL
Occupation
EE
Just looked at a job where the inspector required gfi breakers instead of allowing receptacles because he considered moving a countertop microwave to reset the receptacle “not readily accessible”
The article 100 definition of Readily Accessible says "Capable of being reached quickly for operation, renewal, or inspections without requiring those to whom ready access is requisite to take actions such as to use tools (other than keys), to climb over or under, to remove obstacles, or to resort to portable ladders, and so forth."

Notice that the word "remove" was chosen for the definition and not the more broadly applicable word "move". To remove the microwave from the countertop would be to take it off and place it somewhere else. If the microwave can be shifted to allow access to the receptacle and still remain on the counter then it has not been removed.

Also, it sounds very likely that the GFCI receptacle is more "Capable of being reached quickly", reset, and put in operation in much less time than going to a breaker in a panel to do so.
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
The article 100 definition of Readily Accessible says "Capable of being reached quickly for operation, renewal, or inspections without requiring those to whom ready access is requisite to take actions such as to use tools (other than keys), to climb over or under, to remove obstacles, or to resort to portable ladders, and so forth."

Notice that the word "remove" was chosen for the definition and not the more broadly applicable word "move". To remove the microwave from the countertop would be to take it off and place it somewhere else. If the microwave can be shifted to allow access to the receptacle and still remain on the counter then it has not been removed.

Also, it sounds very likely that the GFCI receptacle is more "Capable of being reached quickly", reset, and put in operation in much less time than going to a breaker in a panel to do so.
Yeah, these could easily be slid over to access the receptacles! Gives inspectors a bad name when they are that nit picky. A paper towel holder sitting front of an outlet would have met his definition of “inaccessible” LOL!
 

retirede

Senior Member
Location
Illinois
Yeah, these could easily be slid over to access the receptacles! Gives inspectors a bad name when they are that nit picky. A paper towel holder sitting front of an outlet would have met his definition of “inaccessible” LOL!

Hey, have you been in my kitchen?!
78809cf0d4eeff4a91a478d5a4a2f866.jpg
 

retirede

Senior Member
Location
Illinois
It's good your plug is in the bottom location, otherwise it would be blocking the reset button and thus be in violation also.

It does block the test button. I’ll tell the wife she has to unplug her fitness tracker charger ever 30 days so I can test the receptacle!
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Is the microwave in a box built for it or is it sitting on the counter? If it is on the counter then the inspector is wrong otherwise I agree with him.
 