(B) Other Than Dwelling Units. All 125-volt, single-phase, 15- and 20-ampere receptacles installed in the locations specified in (1) through (5) shall have ground-fault circuit-interrupter protection for personnel:
(1) Bathrooms
(2) Kitchens
(3) Rooftops
(4) Outdoors
Exception No. 1 to (3) and (4): Receptacles that are not readily accessible and are supplied from a dedicated branch circuit for electric snow-melting or deicing equipment shall be permitted to be installed without GFCI protection.
Exception No. 2 to (4): In industrial establishments only, where the conditions of maintenance and supervision ensure that only qualified personnel are involved, an assured equipment grounding conductor program as specified in 590.6(B)(2) shall be permitted for only those receptacle outlets used to supply equipment that would create a greater hazard if power is interrupted or having a design that is not compatible with GFCI protection.
(5) Sinks — where receptacles are installed within 1.8 m (6 ft) of the outside edge of the sink.
Exception No 1 to (5): In industrial laboratories, receptacles used to supply equipment where removal of power would introduce a greater hazard shall be permitted to be installed without GFCI protection.
Exception No 2 to (5): For receptacles located in patient care areas of health care facilities other than those covered under 210.8(B)(1), GFCI protection shall not be required.
The GFCI can share a neutral on the line side but not the load side.
Look at art.210.8(B) for GFCI requirements for non dwelling
A gfci recep. has a line and load terminals. A gfci breakers line side is the buss bar and the load terminals go to the circuit.
In the case of a gfci breaker you could use a DP gfci breaker and the load side would work with a MWBC.
In the case of a GFCI recep. tyou could not connect the load side of a GFCI to the second circuit of a MWBC. You would have to make that connection on the line side of the device.
So if I have other non GFCI receptcales on the MWBC I can connect these receptacles on the load side terminals of the initial GFCI receptacle and these receptacles will then be considered GFCI protected?
However if the other receptacles are GFCI recepts then they must be connected to the line side of the first GFCI recpt? They could use the same neutral but would just need to be connected on the line side of the recpt?
Can you explain the reason for this?
Absolutely.So if I have other non GFCI receptcales on the MWBC I can connect these receptacles on the load side terminals of the initial GFCI receptacle and these receptacles will then be considered GFCI protected?
Yes. A shared neutral must be split ahead of each 2-wire-supplied GFCI receptacle, effectively pigtailed as you would with any shared neutral.However if the other receptacles are GFCI recepts then they must be connected to the line side of the first GFCI recpt? They could use the same neutral but would just need to be connected on the line side of the recpt?
A GFCI device trips when the current in one conductor is not returned by another circuit conductor(s). All circuit conductors must pass through the current-sensing ring in the GFCI.Can you explain the reason for this?
Gesundheit!You would not need gfci recep. on the load side of a gfci. You would install
Absolutely.
Yes. A shared neutral must be split ahead of each 2-wire-supplied GFCI receptacle, effectively pigtailed as you would with any shared neutral.
A GFCI device trips when the current in one conductor is not returned by another circuit conductor(s). All circuit conductors must pass through the current-sensing ring in the GFCI.
A shared neutral has no way of knowing how much of its current is being supplied by its line conductor, and how much of it by another, so all current will appear as an imbalance.
How about for a GFI breaker? How does it see the neutral current coming back? Can you used a shared neutral with circuits protected from GFI breakers?
Yes. What matters is that only a two-wire (no shared conductors) circuit be connected to the load terminals of a GFCI receptacle.If however there are other receptacles being fed from a second hot circuit then the shared neutral needs to be connected onto the line side of the GFI receptacle. As long as it is connected on the line side then I assume you can use the same neutral to feed other GFI's downstream of the first using a second circuit for the other receptacles.
Only with a 2-pole GFCI breaker, which passes all of the circuit conductors through the current-sensing ring.How about for a GFI breaker? How does it see the neutral current coming back? Can you used a shared neutral with circuits protected from GFI breakers?