chris kennedy
Senior Member
- Location
- Miami Fla.
- Occupation
- 60 yr old tool twisting electrician
I just got home from a trouble call about partial power at a health care facility I finaled a few months ago. 3 phase 480 ATS MTS. Both MDP and MTS have 1000 GFI amp mains. Short time delay is set at .1 sec. as per my PE. I found B phase jack from POCO dropped about 6:30 pm tonight. The ATS showed a ground fault happened at 10:48 AM. This tripped the GFI relay in the ATS which also is set at .1 sec. GF pickup on breakers is set at .1s 30. So there was no transfer. The relay was factory preset(Lakeshore). I will contact my PE tomorrow. Any input?