GFI tripping in hair salon

Status
Not open for further replies.

rp9ball

Member
Location
WI
120/208 system. There are 6 stations. There are 2 networks (4 wire in EMT) feeding these stations. Network #1 serves stations 1, 2, and 3. Network #2 serves stations 4, 5, and 6. If station 1 is running a hair dryer and station 4 starts a clippers, its trips the GFI on the hair dryer. It is not limited to any 2 stations. They have tried different equipment (hair dryers and clippers) and still have the same problem. Any ideas why this is happening and how to correct it?

Thanks
 
Do you mean that GFCI breakers (as opposed to GFCI receptacles) are tripping? If so, how do you know that it is their ground fault electronics that are causing them to trip? Is it possible that the circuits are just overloaded, and that turning on one more clipper is enough to push it over the edge?
 
Each station has its own 20 amp circuit. The GFI's that trip out are the ones on hair dryer itself where the GFI is installed on the cord end.
 
Re: GFI tripping in hair salon

rp9ball said:
120/208 system. If station 1 is running a hair dryer and station 4 starts a clippers, its trips the GFI on the hair dryer. It is not limited to any 2 stations. They have tried different equipment (hair dryers and clippers) and still have the same problem. Any ideas why this is happening and how to correct it?

I don't know if this matters, but are you sharing the neutral and or are the two stations on the same phase?
 
Each network has its own neutral. And good point station 1 and station 4 are on the same phase, but seperate networks.
 
Very interesting situation. Haven't come across this myself, but it sounds more like 'chance' than anything. What I've found, after a little internet research, is that hair dryer cords might be GFCIs, but there also might be one-time-use immersion protection or a cut-down (two wire) version of a GFCI called an ALCI. Here's a quote from the Conair site:

Conair? manufactures its hairdryers with two different kinds of safety plugs. The ALCI is known as an Appliance Leakage Current Interrupter. This unit has the "Reset" button and the "Test" button. The circuit is looking for leakage of current between the two conductors. This unit sometimes trips when lights are turned on and off, when the dryer is plugged in, or when a new dryer is taken out of the box and plugged in by the consumer who doesn?t know how to operate the RESET feature. An IDCI refers to Immersion Detector Current Interrupter. This unit trips only when the dryer has been immersed in water. The dryer should never be used again after immersion because of the potential dangers a water-damaged unit presents to consumers. That is why this unit trips once and is not resettable -- because it shouldn?t be used again!

Very little information about ALCIs on the web. But, basically, it is 'like' a commercial GFCI with current transformers and a comparator. Unlike a typical GFCI, the ground is connected only to the applicance and not the electrical EGC. They are apparently prone to nuisance trips. Snapping on clippers makes perfect sense, with capacitance in the raceway and both circuits next to each other at the panel. I suppose you could try another circuit, to test the things to see 'how' sensitive it is. Don't know whether these things wear out, but it would be interesting to call the hair dryer manufacturer to see what they have to say. ("We went to ALCIs because people either buy new dryers or cut them off so we have no product liability" sound likely?)
 