sparkync
Senior Member
- Location
- North Carolina
I have had to pull a new underground UF cable, to a "sign light" that was damaged underground somewhere. It was fed previously from another junction box for "flagpole" lighting. I had to run the new feed, straight from the electrical panel on the wall for "main entrance" to this project. There is a photo cell on the side of the panel and I installed a "GFCI" outlet under the panel, where there was just a regular outlet. I tried tying everything on the load side of the GFI, but it won't hold. I fed the "line side" hot of the "GFCI" from the breaker, then the "load side" hot I fed to the photo cell, and the "hot" wires to the flag pole light and the sign light, went to the red wire coming off the photo cell. I tied the "load neutral" off the GFCI, to the neutral on the photo cell. I first tied the "neutrals" to the flagpole light and sign light, with this same neutral, but it would not hold, so I ran a "separate" neutral, up to the neutral bar for the flagpole light and sign light. It still would not hold. I'm not sure whether the neutral connections are causing this, or if maybe there is a problem with the existing wire underground. It works alright when I hook it up without the GFCI. If you can understand my description, do you have any ideas? The circuit really needs to be on the GFCI, because of "depth" of the wire, etc.. The only other thing I can think of, is just feed the photo cell hot before I go through the GFCI outlet, and go to the "line side" of the outlet from the photo cell. Haven't tried it this way. I was thinking the photo cell needed to go through the GFCI, but maybe not. Thanks for your input.