A GFCI receptacle's test button works by connecting a resistor from the hot wire after the current sensor to the neutral ahead of the current sensor, which mimics someone receiving a shock.I have a GFI recept in a kitchen on a 2 wire system-no ground.The GFI will trip when you press the test button.It will not trip using a plug in GFI tester.My question is would it make any difference to install GFI brkr?I don't think it will. I'd appreciate any input.Thanks
Thanks for the feedback.I thought the problem was probably with the 2-wire system,not having a ground wire.Thanks
I have a GFI recept in a kitchen on a 2 wire system-no ground.The GFI will trip when you press the test button.It will not trip using a plug in GFI tester.My question is would it make any difference to install GFI brkr?I don't think it will. I'd appreciate any input.Thanks
that is the way it should be. the plug in testers are pretty much useless for testing the GFI part of a receptacle. use the test button on the receptacle.
Thanks for the input. I didn't realize those GFI testers test between hot and ground.I thought they tested between hot and neutral mimicking how the device actually works.
The reason for the stickers is to give code making panel and inspectors a warm fuzzy feeling. Typical user has no clue what they mean.All 3 prong receptacles that are GFI protected but only have two wire circuits should have stickers on them that read "GFI Protected / No Equipment Ground". I would guess that part of the reason for this is because when you put a plug tester in such a receptacle, it will not trip the tester... The only way to test those receptacles properly is to trip the Upstream GFI and verify power is dead.
GFI receptacles and Breakers work perfectly well with two wire systems, the ground wire is irrelevant for their operation
Any current between the "hot" and "neutral" of the receptacle or "load terminals" is seen as normal expected load. Any current that leaks outside that path is abnormal, and once it exceeds 4-6 mA trips the device. The test button sends test current outside the protected path, one side of "line" conductors to opposite side of "load" conductors". This path is outside of the current transformer that monitors the intended current path.Thanks for the input. I didn't realize those GFI testers test between hot and ground.I thought they tested between hot and neutral mimicking how the device actually works.
Well, there is another way. I use my solenoid tester to check for GFCI protection by plugging one probe in the receptacle's hot slot and grounding the other probe. Anything from an extension cord to a nearby sink's faucet (presuming metal piping) to any nearby grounded surface will work.The only way to test those receptacles properly is to trip the Upstream GFI and verify power is dead.
Digital meter with a low impedance setting works also. Or any load you can imagine over 6 mA connected to a point inside and a point outside the GFCI protected circuit will trip it.Well, there is another way. I use my solenoid tester to check for GFCI protection by plugging one probe in the receptacle's hot slot and grounding the other probe. Anything from an extension cord to a nearby sink's faucet (presuming metal piping) to any nearby grounded surface will work.
I think the real reason for those stickers is 250.114....something no user has any clue about, and most inspectors don't either. They added Informational Note #2 following 406.4(D)(2) in the 2017 code to call attention to the requirements in 250.114.The reason for the stickers is to give code making panel and inspectors a warm fuzzy feeling. Typical user has no clue what they mean.
...
I think the real reason for those stickers is 250.114....something no user has any clue about, and most inspectors don't either. They added Informational Note #2 following 406.4(D)(2) in the 2017 code to call attention to the requirements in 250.114.
I'll stand by what I previously said. Electricians will see that sticker and realize there isn't an EGC, they might even say to themselves 'someone must know the codes'. Most users won't know or care what that sticker means. Inspectors will be happy because code was followed though it didn't really matter one bit on this one.I think the real reason for those stickers is 250.114....something no user has any clue about, and most inspectors don't either. They added Informational Note #2 following 406.4(D)(2) in the 2017 code to call attention to the requirements in 250.114.
I'll stand by what I previously said. Electricians will see that sticker and realize there isn't an EGC, they might even say to themselves 'someone must know the codes'. Most users won't know or care what that sticker means. Inspectors will be happy because code was followed though it didn't really matter one bit on this one.
Don't confuse the "self testing" feature with the procedure of pressing the test button, they are not the same thing. Pressing that test button actually creates a real unbalance current condition and the device should mechanically open the circuit.I had a home inspector write up the GFCI receptacle in the kitchen did not trip with his tester, even though it was marked with those stickers, and the GFCI not only work, it was one of the new self-testing ones as well.
Other people's children....lol