I thought all outdoor repceptacles didn't have to be GFI.
You're right. The basic formula for the codebook is simple: A rule is given. Unless the rule has an exception, or is modified later in the codebook, then it applies in all situations described.
So, looking at this section, 210.8, we'll take it from the top:
(A) Dwelling Units. All 125-volt, single-phase, 15- and 20-ampere receptacles installed in the locations specified in (1) through ( shall have ground-fault circuit-interrupter protection for personnel.
So, for starters, every single 15A and 20A receptacle listed is required to have GFCI protection.
- (A)Dwelling Units
- (B)Other than Dwelling Units
So, once you decide if it is a dwelling unit or not, you move on.
You're working outdoors.
So, every single 15A and 20A receptacle outdoors is required to have GFCI protection.
But, there is an exception:
Exception to (3): Receptacles that are not readily accessible and are supplied by a dedicated branch circuit for electric snow-melting or deicing equipment shall be permitted to be installed in accordance with 426.28.
Now, before you jog down the bunny trail to 426.28, just ask yourself: "Are any of the receptacles I am working with for de-icing equipment?" If the answer is no, then you can't make use of the exception this time. Further, if any aspect of the exception doesn't match your scenario (not readily accessible, dedicated circuit), then you can't use the exception.
Does that make sense?
The receptacle itself doesn't need to be a GFCI. But it does need GFCI protection. There are times when the specific wording may call for a GFCI receptacle itself - but they are few and far between. For most occasions, just having the protection is required.