Gfi

Status
Not open for further replies.

hot wire

Member
Location
bumpass,Va
boy did i screw up i ran all this 12 -3 to these recp started trimming out some outside gfi guys wants 2 ckts per box went to hook up load side guess my brain kicked in reg outlets wont work with 2 ckts and 1 netural on the load side of the gfi..1 st way to fix all gfi hooked up on the line side .2nd 2 pole gfi breaker wuth reg out lets put in. how would yall fix this mess . let the owner try to decide to much he told us he was going 2 put all gfi in know its 2 gfi and 2 reg outlets..same problem in bathroms and kitchen. how much does a 2 pole 20 amp gfi breaker cost vs 20 amp gfi recp...
 
boy did i screw up i ran all this 12 -3 to these recp started trimming out some outside gfi guys wants 2 ckts per box went to hook up load side guess my brain kicked in reg outlets wont work with 2 ckts and 1 netural on the load side of the gfi..1 st way to fix all gfi hooked up on the line side .2nd 2 pole gfi breaker wuth reg out lets put in. how would yall fix this mess . let the owner try to decide to much he told us he was going 2 put all gfi in know its 2 gfi and 2 reg outlets..same problem in bathroms and kitchen. how much does a 2 pole 20 amp gfi breaker cost vs 20 amp gfi recp...



What kind of panel is it? The breaker is most likely your best bet
 
boy did i screw up i ran all this 12 -3 to these recp started trimming out some outside gfi guys wants 2 ckts per box went to hook up load side guess my brain kicked in reg outlets wont work with 2 ckts and 1 netural on the load side of the gfi..1 st way to fix all gfi hooked up on the line side .2nd 2 pole gfi breaker wuth reg out lets put in. how would yall fix this mess . let the owner try to decide to much he told us he was going 2 put all gfi in know its 2 gfi and 2 reg outlets..same problem in bathroms and kitchen. how much does a 2 pole 20 amp gfi breaker cost vs 20 amp gfi recp...

Boy, did i screw up! I ran all this 12-3 to these receptacles. Started trimming out some outside gfi. Guys wants 2 ckts per box went to hook up load side. Guess my brain kicked in reg outlets wont work with 2 ckts and 1 netural on the load side of the gfi.

1 st way to fix : all gfi hooked up on the line side. 2nd way : 2 pole gfi breaker with regular outlets put in.

How would you fix this mess? Let the owner try to decide? "Too much," he told us. He was going to put all gfi in. Now it's 2 gfi and 2 reg outlets. Same problem in bathroms and kitchen.

How much does a 2 pole 20 amp gfi breaker cost vs 20 amp gfi recp?















Spend $30-40 for a 2-pole GFCI breaker and be done with it.
 