I don't think the code requires GFI protected receptacles in mechanical rooms, unless of course it was within 6' from the edge of a sink (such a service sink or mop sink.) Then it would be required by 210.8(B)(5).
 
Its doesnt really say a mech room..it refers you to 260.63 which refers you back to 210.8

I think you mean 210.63, which requires a receptacle for servicing to be located within 25' of HVAC equipment.

That receptacle wouldn't need GFI protection per 210.8 unless it was located on a roof, in a kitchen or bathroom, outdoors, or within 6' from the outside edge of a sink.
 