Re: GFIC Protection on Power factor Correction Equipment
I assume you are talking about "GFCI" or a "Ground Fault Circuit Interrupter". I have also heard it called "GFI" for "Ground Fault Interrupter". However, "GFIC" is a new one to me.
I don't see any exceptions in the code for power correction equipment. However, if you have a 1000 amp feeder, isn't there a 1000 amp service that already has a GFCI on it? 215.10 exception #3 states "The provisions of this section shall not apply if ground -fault protection of equipment is provided on the supply side of the feeder." Thus, if the service is protected, I don't think you need additional protection. (Healthcare is an exception to this)
You might also consider dividing the capacitors and feeders into a couple smaller 800 amp units.
1000 amps seems like a lot for PF correction. My first impulse would be to say if your PF is 0.8 for example, you would only need 20% of the load ampacity to run to the capacitor. In other words, a 1000 amp feeder to a capacitor would correct a 5000 amp load. Or am I missing something?
Steve