markebenson
Senior Member
- Location
- fl
Single Phase panel, 4 20a circuits
For this stage setup I have removed 4 GFI outlets from the stage, replaced them with standard 20a outlets. I have installed 4 GE THQL1120GFTP in the panel. The first two 20 gfi I installed tripped the gfi, the white coil wire connected to the neutral bar as in should be.
THE CONNECTIONS IN THIS PHOTO ARE FOR TROUBLESHOOTING PURPOSES ONLY
The second set of two gfi do not trip the GFI, white coil wire temp connected to the ground bar for testing
In the next photo i have discovered neutrals tied together in this j box. I assume this is what may be causing my issues.
Thank you for your help!
For this stage setup I have removed 4 GFI outlets from the stage, replaced them with standard 20a outlets. I have installed 4 GE THQL1120GFTP in the panel. The first two 20 gfi I installed tripped the gfi, the white coil wire connected to the neutral bar as in should be.
THE CONNECTIONS IN THIS PHOTO ARE FOR TROUBLESHOOTING PURPOSES ONLY
The second set of two gfi do not trip the GFI, white coil wire temp connected to the ground bar for testing
In the next photo i have discovered neutrals tied together in this j box. I assume this is what may be causing my issues.
Thank you for your help!