I know this is a touchy subject, but I am trying to clarify the issue at least in my mind...
It is my understanding that in a 480/277 Wye system provided by the utility company, NEC 250.24(C) requires the neutral conductor to be brought to the service disconnect even if there are no L-N loads to be served. It is also my understanding that NEC 250.24(A)(2) requires a bonding connection both at the transformer and the Main Service enclosure. If the Neutral conductor is not carried any further than the Main Service Disconnect for all practical purposes the system is a 3 phase, 3 wire right? If this is the case and if the system has an optional standby generator, the generator can be grounded at the generator location and the GEC connected to the utility power GEC and still be considerd an SDS right?
And along the same lines if this service is required to have GFP, this protection is not compromised by the generator grounding...?
And as last question if the generator is protected by a 1200 A breaker does it need to have GFP...? I am guessing it doe based on NEC 215.10, but I would like to hear any dissenting apinions
It is my understanding that in a 480/277 Wye system provided by the utility company, NEC 250.24(C) requires the neutral conductor to be brought to the service disconnect even if there are no L-N loads to be served. It is also my understanding that NEC 250.24(A)(2) requires a bonding connection both at the transformer and the Main Service enclosure. If the Neutral conductor is not carried any further than the Main Service Disconnect for all practical purposes the system is a 3 phase, 3 wire right? If this is the case and if the system has an optional standby generator, the generator can be grounded at the generator location and the GEC connected to the utility power GEC and still be considerd an SDS right?
And along the same lines if this service is required to have GFP, this protection is not compromised by the generator grounding...?
And as last question if the generator is protected by a 1200 A breaker does it need to have GFP...? I am guessing it doe based on NEC 215.10, but I would like to hear any dissenting apinions