malachi constant
Senior Member
- Location
- Minneapolis
I am designing distribution for a large school (about 500,000 SF). The mechanical engineer is leaning towards a distributed chiller system (a number of 400 to 800 MCA chillers located around perimeter and on roof). I was penciling in a couple 1200A MLO distribution switchboards to feed multiple chillers, then realized since these are 480V and over 1000A they would need GFP, which then triggers the need for a main - correct? Or are you required to put the GFP ahead of the feeder, which would put it at the 1200 BPS in the main switchboard, and would eliminate the need for a main at the DP? A main is not a terrible option, but it does increase cost and footprint. Thinking it through, I'm guessing putting GFP at the upstream OCPD is more common then adding a main the downstream equipment - right?
Another option would be feeding more chillers direct from the main service switchboard so that I have no downstream equipment over 1200A. This would eliminate the need for any GFP beyond the main service disconnect - and in my experience downstream GFP trip with enough frequency it seems good to minimize them.
For whatever reason I've managed to avoid thinking about downstream GFP for most of my career and am curious how the design community approaches larger scale 480V systems like this. Minimize GFP (keep equipment at 800A) for nuisance tripping purposes? Ignore concerns of nuisance tripping and just design to minimize feeder/distrubution costs? Does anyone see downstream GFP as something that should be embraced so as to increase safety, as opposed to avoided due to nuisance concerns?
I'm leaning towards the "keep distribution below 800A" - the largest chiller is closest to the service. I think all the rest are far enough apart from each other and closer to 400A that this is justifiable. But your thoughts/experience is appreciated. Thanks in advance!
Another option would be feeding more chillers direct from the main service switchboard so that I have no downstream equipment over 1200A. This would eliminate the need for any GFP beyond the main service disconnect - and in my experience downstream GFP trip with enough frequency it seems good to minimize them.
For whatever reason I've managed to avoid thinking about downstream GFP for most of my career and am curious how the design community approaches larger scale 480V systems like this. Minimize GFP (keep equipment at 800A) for nuisance tripping purposes? Ignore concerns of nuisance tripping and just design to minimize feeder/distrubution costs? Does anyone see downstream GFP as something that should be embraced so as to increase safety, as opposed to avoided due to nuisance concerns?
I'm leaning towards the "keep distribution below 800A" - the largest chiller is closest to the service. I think all the rest are far enough apart from each other and closer to 400A that this is justifiable. But your thoughts/experience is appreciated. Thanks in advance!