I agree that GFP is a good idea BUT if it cannot be properly coordinated with other devices, it is a poor option. In POCO high-voltage work, we often use a ground trip that is 50% of the phase trip
It can be coordinated with the majority of OCPS in a building and a GFP at 408/277 solidly grounded system beats the heck of the devastation of an arcing ground fault.