I am doing a QC review for a new high rise building. The main switchboard is shown with fused disconnects (incoming main and all feeders). Same for the emergency switchboard. Two questions:
My answers are, in order, "I don't know and I can't understand how," and "No." What say ye?
- Since the service is 4000 amps at 480V, article 240.13 requires Ground Fault Protection for Equipment (GFPE) for the main building disconnecting means. Can that be achieved with a fused disconnect?
- Backup generator feeds a four section vertical switchboard. The four sections feed a fire pump, another fire pump, an NEC 700 ATS, and an NEC 701 ATS. The 700 ATS feeds the emergency switchboard, which has a fused disconnect as its main OCPD. They are showing it with GFPE. Is that needed?
My answers are, in order, "I don't know and I can't understand how," and "No." What say ye?