Please see attached sketch. I have High Rise that has 277/480V main service switchboard 2000A.
The switchboard feeder has Bkr#1 Standby Load and second feeder has Bkr#2 to emergency life and safety load. Downstream has ATSs and emergency generator.
As I read it emergency systems are Not allowed to be on Ground fault protection only detection is allowed NEC 2017 section 709.6(D)
However NEC 2017 section 215.10 requires GFPE on feeder
Its confusing Questions:
1. would GFPE be allowed on in swtichboard BKr#2 that feeds emergency load or Bkr #1 that feeds standby load attached sketch or not?
2. Would GFPE be allowed at the generator breaker?
The switchboard feeder has Bkr#1 Standby Load and second feeder has Bkr#2 to emergency life and safety load. Downstream has ATSs and emergency generator.
As I read it emergency systems are Not allowed to be on Ground fault protection only detection is allowed NEC 2017 section 709.6(D)
However NEC 2017 section 215.10 requires GFPE on feeder
Its confusing Questions:
1. would GFPE be allowed on in swtichboard BKr#2 that feeds emergency load or Bkr #1 that feeds standby load attached sketch or not?
2. Would GFPE be allowed at the generator breaker?