Hello, I have a very unique situation that in my 20+ years have never came across. AHU= Air Handler Unit
We have a NEW Fire System installed in a Mini Storage Building where everything is metal. On the SLC circuit which is "disconnected from the panel" Using my meter on Ohms, I get nothing shorted across the pair and neither leg has any short to ground. However, when metering A/C voltage I get 0.030-0.125 VAC on either leg to ground. I have isolated the issue down to the AHUs. Here is what I am doing.
All AHUs in the building have their breakers on at the electric panel. I have the disconnect at the AHU off on the AHUs creating the problem. In this scenario, I read NO A/C VOLTAGE to ground. BUT as soon as I turn on 1 or more of the problem AHUs I see the AC Voltage. Interestingly turning on several AHUs at the disconnect increases the voltage but then sometimes reduces the voltage. I'm not sure if it's because the inductance is getting dispersed or what.... Any thoughts on the cause of the Induced A/C Voltage? The Panel manufacturer says any A/C voltage on the SLC circuit for more than 30Sec can Blow the FACP.
We have a NEW Fire System installed in a Mini Storage Building where everything is metal. On the SLC circuit which is "disconnected from the panel" Using my meter on Ohms, I get nothing shorted across the pair and neither leg has any short to ground. However, when metering A/C voltage I get 0.030-0.125 VAC on either leg to ground. I have isolated the issue down to the AHUs. Here is what I am doing.
All AHUs in the building have their breakers on at the electric panel. I have the disconnect at the AHU off on the AHUs creating the problem. In this scenario, I read NO A/C VOLTAGE to ground. BUT as soon as I turn on 1 or more of the problem AHUs I see the AC Voltage. Interestingly turning on several AHUs at the disconnect increases the voltage but then sometimes reduces the voltage. I'm not sure if it's because the inductance is getting dispersed or what.... Any thoughts on the cause of the Induced A/C Voltage? The Panel manufacturer says any A/C voltage on the SLC circuit for more than 30Sec can Blow the FACP.