Give the Ampacities of The Following Copper Conductors. Not More than 3 Conductors in a raceway with THHN Insulation Based on the 2017 NEC Code

Status
Not open for further replies.

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Tell us what you think and how you came to your answer, we will not do your homework for you.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
As far as the conductors ampacity, that is correct.
There are other limiting factors as far as allowable termination ratings.

(opps sorry roger posted at the same time)
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
In my view the question is not valid as to use the tables the temp has to be stated. It should read what is the ampacity at X temp. And as larry stated it would also need to state CU or AL.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
If this is a test question, those who have taken an electrical exam know they are looking for THEIR answer. There is, most times, different factors that could effect the answer. So you sort of have to train your mind to leave out things that were not mentioned in the question.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If this is a test question, those who have taken an electrical exam know they are looking for THEIR answer. There is, most times, different factors that could effect the answer. So you sort of have to train your mind to leave out things that were not mentioned in the question.
Having taken a few licensing exams over the years this is good advice. (y)

From the question you have three factors: conductor size(s), an insulation type, and not more than 3 CCC's in a raceway. That's it, don't complicate it.
 