Gluing PVC conduit

Status
Not open for further replies.

T-Wragg

Senior Member
Location
Paradise, California, USA
Occupation
Electrical Contractor
I just had a conversation with another electrician who said that PVC conduit had to be properly supported based on the spacing dictated in the code but it is not required to be glued. I was under the impression that it had to be glued to be considered to be a complete conduit system. Is it required to be glued? Thanks
 

tkb

Senior Member
Location
MA
I think he has been sniffing the glue.

352.48 Joints
All joints between lengths of conduit, and between conduit
and couplings, fittings, and boxes, shall be made by an approved
method.

Rigid Nonmetallic Schedule 40 and Schedule 80
PVC Conduit (DZYR)
[Rigid nonmetallic] Schedule 40 conduit is suitable for
underground use by direct burial or encasement in concrete.
Schedule 40 conduit is also suitable for aboveground
use indoors or outdoors exposed to sunlight and
weather where not subject to physical damage.
Schedule 80 conduit has a reduced cross-sectional
area available for wiring space and is suitable for use
wherever Schedule 40 conduit may be used. The marking
“Schedule 80 PVC” identifies conduit suitable for
use where exposed to physical damage and for installation

on poles in accordance with [
352.10(F) and352.12(C) of the] NEC.

Unless marked for higher temperature, rigid nonmetallic

conduit is intended for use with wire rated 75?C or
less including where it is encased in concrete within
buildings and where ambient temperature is 50?C or less.
Where encased in concrete in trenches outside of buildings

it is suitable for use with wires rated 90?C or less.


Listed PVC conduit is inherently resistant to atmosphere


containing common industrial corrosive agents
and will also withstand vapors or mist of caustic, pickling
acids, plating bath and hydrofluoric and chromic acids.



PVC conduit and elbows [and bends] (including

couplings) that have been investigated for direct exposure
to other reagents may be identified by the designation
“Reagent Resistant” printed on the surface of the
product. [Further information on reagent resistance may
be found in the UL
Electrical Construction Materials Directory


and in ANSI/UL 651, Schedule 40 and 80 Rigid PVC Conduit.]



PVC conduit is designed for connection to couplings,

fittings, and boxes by the use of a suitable
solvent-type cement. Instructions supplied by the solvent-
type cement manufacturer describe the method of
assembly and precautions to be followed. [Fittings for
use with Rigid Polyvinyl Chloride Conduit: Type PVC
are covered under UL category (DWTT) Conduit Fittings.]






 