We have an issue on parallel 500 MCM cables at a hospital. Seems the "electrician" pulled them many months early and failed to properly protect them where they exited a conduit. This is just one of numerous issues with this electrician.
We are requiring him to megger them. Voltage is 480V, so we plan to megger at 1000V for 60 seconds, phase to phase and ground, six tests per conductor.
What values do you typically use for go/marginal/no go?
The last time we had testing done typically the cables were 400meg ohms to infinity. I have a bad feeling these will test out low. But how low to require the electrician to re-pull the cables? I know he will really fight re-pulling. I expect that if we consider the readings "too low" we likely will need to bring in a specialized testing contractor. Could be nasty.
We have reviewed some of the literature and some of the "acceptable" values look way too low to what I am used to seeing.
Thanks ahead of time,
RC
We are requiring him to megger them. Voltage is 480V, so we plan to megger at 1000V for 60 seconds, phase to phase and ground, six tests per conductor.
What values do you typically use for go/marginal/no go?
The last time we had testing done typically the cables were 400meg ohms to infinity. I have a bad feeling these will test out low. But how low to require the electrician to re-pull the cables? I know he will really fight re-pulling. I expect that if we consider the readings "too low" we likely will need to bring in a specialized testing contractor. Could be nasty.
We have reviewed some of the literature and some of the "acceptable" values look way too low to what I am used to seeing.
Thanks ahead of time,
RC