If thirty-five 14 AWG TW current carrying conductors are installed in a raceway, the applicable adjustment factor of 0.4 would limit the ampacity of the conductors to 8 amps.
Assuming the building where this occurs employs circuit breakers for overcurrent protection, would the next higher overcurrent device be 15 (the next higher circuit breaker) or 10,the next higher standard fuse size?
Any help would be appreciated.
Brian Dolan