"Good engineering practice" Article in the NEC

Status
Not open for further replies.

egurdian3

Member
Location
Germantown, MD
I'm trying to back up the phrase "Good engineering practice recommends not to load electrical equipment beyond 80% of full capacity". Which article has this requirement?
Thanks.
 
If you looked, you could find something in the NEC about sizing circuits / feeders for continuous loads at 125% (inverse of 80%).

You could also probably find something in UL489 for molded case breakers (I suspect) about loading them at 80% continuous load.

But as Charlie said, so such requirement as you have requested.
 
Take a look at 210.19(A)(1) and 215.2(A)(1). Both require conductors to have an ampacity at least equal to 100% of the continuous load plus 125% of the non-continuous load.
 