Ragin Cajun
Senior Member
- Location
- Upstate S.C.
I have been requested to provide a second engineering opinion on an engineer's stamped drawings. My client's electrician had many "concerns" with the drawings. I found numerous" issues" with the drawings and in reviewing them for my client, I have tried to be "low key".
Aside from numerous other issues, I have several questions for the group.
1. When circuiting lights, receptacles, and other electrical loads, do you place the circuit ID beside each device on the drawings? I think this is good engineering practice. Otherwise the electrician must hand mark-up the paper drawings to properly circuit the loads. This particular set of drawings did not do that.
2. I have always put light and receptacles on separate circuits. I don't want the occupant in the dark when the device connected to the receptacle trips the breaker. Again, this particular set of drawing put both on the same circuit.
3. I have always left either spare breakers or spare spaces in any panel board I layout. This set of drawings had a 54 circuit panel board with ONE spare! Come on man, that is poor engineering design! I thought this was in the code but couldn't fine it.
4. On panel board schedules, I always put individual load data for each circuit and sum each phase up and the overall total. How else can you know that they are reasonably balanced and know the total connected load? Again, not done on these drawings.
Am I just being picky, or what? I know what I would expect if I was installing the job.
Thanks ahead for your comments.
RC
Aside from numerous other issues, I have several questions for the group.
1. When circuiting lights, receptacles, and other electrical loads, do you place the circuit ID beside each device on the drawings? I think this is good engineering practice. Otherwise the electrician must hand mark-up the paper drawings to properly circuit the loads. This particular set of drawings did not do that.
2. I have always put light and receptacles on separate circuits. I don't want the occupant in the dark when the device connected to the receptacle trips the breaker. Again, this particular set of drawing put both on the same circuit.
3. I have always left either spare breakers or spare spaces in any panel board I layout. This set of drawings had a 54 circuit panel board with ONE spare! Come on man, that is poor engineering design! I thought this was in the code but couldn't fine it.
4. On panel board schedules, I always put individual load data for each circuit and sum each phase up and the overall total. How else can you know that they are reasonably balanced and know the total connected load? Again, not done on these drawings.
Am I just being picky, or what? I know what I would expect if I was installing the job.
Thanks ahead for your comments.
RC