Do you know if there is a code to reference it to.No it can have overcurrent protection. Simplest way (cheapest) is a circuit breaker with the proper labels.
Welcome to the Forum.
230.85 Emergency Disconnects.
For one- and two-family dwelling units, all service conductors shall terminate in disconnecting means having a short-circuit current rating equal to or greater than the available fault current, installed in a readily accessible outdoor location. If more than one disconnect is provided, they shall be grouped. Each disconnect shall be one of the following:
(1) Service disconnects marked as follows:
EMERGENCY DISCONNECT,
SERVICE DISCONNECT
(2) Meter disconnects installed per 230.82(3) and marked as follows:
EMERGENCY DISCONNECT,
METER DISCONNECT,
NOT SERVICE EQUIPMENT
(3) Other listed disconnect switches or circuit breakers on the supply side of each service disconnect that are suitable for use as service equipment and marked as follows:
EMERGENCY DISCONNECT,
NOT SERVICE EQUIPMENT
Markings shall comply with 110.21(B).
thanks i dont know how i missed that.It's in 230.85(3). Circuit breakers are clearly listed.
You're welcome. Here's one I did recently. View attachment 2572452
One KO was 3/4" from the back the other 1" from the back so they did not line up hence the offset nipple. At least the bottoms are even.My OCD requires that I ask why not mount the disconnect slightly lower and avoid the offset?
It is not the service disconnect if the label that you put on it says "EMERGENCY DISCONNECT, NOT SERVICE EQUIPMENT".If the 230.85 Emergency Disconnect has overcurrent protection (fused or circuit breaker) then is that NOT considered the first means of OCP??
If a non-fused knife switch disconnect is installed, then it is just the 'Emergency Disconnect/Not service disconnect?
Finding a Non-Fused disconnect that is OVER 10K fault current, I have not seen any.
So, a CB used as the 230.85 compliant disconnect, with the required label, is the Main OCP, and the N/G bonding is within that enclosure,
and 4-wire is installed to the panel, which is treated as a 'sub-panel.
Comments, gentlemen please.
Correct, to go along with the photo I posted in post #6 there are only three conductors run to the panel on the interior which has a 200 amp breaker serving as the service disconnect. All of the GEC's land there as well. The 200 amp breaker on the outside (below) is (as labeled in the post #6 photo) only the emergency disconnect.It is not the service disconnect if the label that you put on it says "EMERGENCY DISCONNECT, NOT SERVICE EQUIPMENT".
If you mark the emergency disconnect that way, you can run three service conductors to the inside service equipment and connect the GEC and the main bonding jumper at the inside service equipment.
There is no physical difference in the two installations. The only thing that changes is the label.
How old is this? Prior to the 2008 NEC a separate structure did not require an EGC run with the feeder when some conditions were met. Looks like an 8 circuit panel with feed through lugs.how Would one view a meter main that has feed thru lugs and provisions for 4 breakers. Installing a breaker into the enclosure to feed a remote barn does that require the egc? The 200 amp breaker shuts off the the provisions for the 4 breakers spaces
One KO was 3/4" from the back the other 1" from the back so they did not line up hence the offset nipple. At least the bottoms are even.
I get the anal part. I was somewhat annoyed that the KO's didn't line up so that I could use a straight nipple.Makes sense. I feel better now!![]()