Good system?

Hv&Lv

Senior Member
I thought you were calculating...
the cable manufacturers have the capacitance of the cables listed, calculate your capacitance on each cable length to each inductor.

that’s why I’m suggesting a higher voltage class cable like a 35kV cable with the lower voltages to get the capacitance down.
that or add shunt reactors...
 

mbrooke

Senior Member
I thought you were calculating...
the cable manufacturers have the capacitance of the cables listed, calculate your capacitance on each cable length to each inductor.

that’s why I’m suggesting a higher voltage class cable like a 35kV cable with the lower voltages to get the capacitance down.
that or add shunt reactors...
I am, and leaning toward this system. However, 35kv cable energized at 33kv would be the simplest and most economical.
 