Gould ITE compatability

Status
Not open for further replies.
Hello everyone, I am looking for breaker compatability for an old Gould W33 PAK Meter Pack. Does anyone out there know which breakers are LISTED for use. I have searched for ITE breakers and can not find them. Siemens dropped the ITE from their logo and the local AHJ will not recognize them. The breakers at issue are 240v 100a 2 pole plug on. Any Ideas? Thanks
 
The Siemens breakers are the direct replacements. If the inspector is refusing to accept them you will need to try and get a letter from Siemens to show the inspector.

Edited to ask........
Do you really need 240 volt breakers? Standard 2 pole breakers are 120/240 volt. The 240 volt version is available but will cost $$$ and probably be special order. As long as the voltage to ground is not over 120 volts the slash rated breakers are acceptable.
 
Last edited:
UL Letters

UL Letters

Here are some UL letters that may help with inspectors
 