My job is at risk over this one--I am the electrical supervisor at an American Army base in Afghanistan. We are subject to NEC 2008, no local codes or regs.
Power is supplied by gen sets, feeding out to I-Line panels and then on to QO 100 and 225 amp panels. Typical building has one I-Line feeding subpanels on the building.
When the Army built the base, they installed one 3 meter segmented ground rod connected to the panel neutral bus by metric 6 AWG equivalent wire at each panel.
When I arrived last winter, I installed an isolated ground bar in each panel and an additional grounding electrode (8 ft rod) at each panel in one of 2 ways:
1--New 6 AWG wire from the ground bar to the new rod. Also relocated the existing ground wire to the new ground bar, thus each panel has more than one grounding electrode conductor and grounding electrode.
2--New 6 AWG wire from the ground bar to and through an acorn clamp on the old rod, then on to the new rod without splices.
I also interconnected all the electrodes on each structure. Sometimes this was by an underground conductor from one panel's rod to another panel's and sometimes it was from one panel's ground bar to the other panel's ground bar.
Today Quality Control reported that I am out of compliance with 250.64(C) because I have created a splice (the ground bar) between electrodes. I am also out of compliance with 250.56 because there are a couple of places the Army had installed more than one ground rod by running one section of wire from the panel to the rod, then a DIFFERENT section of wire from the first rod to the second rod. He also reported that I need to pull the rods up a little, as the connection is not accessible.
He is older and more experienced than me (maybe not saying much as I am 29) but I am not ready to say I am wrong yet. Any comments, especially code references? Can I run more than one GEC to a ground bar? Can I have a splice in rods in series? How do I get 8 ft of rod in contact with soil (250.53G) and have some of it out of the ground?
Thanks!
Power is supplied by gen sets, feeding out to I-Line panels and then on to QO 100 and 225 amp panels. Typical building has one I-Line feeding subpanels on the building.
When the Army built the base, they installed one 3 meter segmented ground rod connected to the panel neutral bus by metric 6 AWG equivalent wire at each panel.
When I arrived last winter, I installed an isolated ground bar in each panel and an additional grounding electrode (8 ft rod) at each panel in one of 2 ways:
1--New 6 AWG wire from the ground bar to the new rod. Also relocated the existing ground wire to the new ground bar, thus each panel has more than one grounding electrode conductor and grounding electrode.
2--New 6 AWG wire from the ground bar to and through an acorn clamp on the old rod, then on to the new rod without splices.
I also interconnected all the electrodes on each structure. Sometimes this was by an underground conductor from one panel's rod to another panel's and sometimes it was from one panel's ground bar to the other panel's ground bar.
Today Quality Control reported that I am out of compliance with 250.64(C) because I have created a splice (the ground bar) between electrodes. I am also out of compliance with 250.56 because there are a couple of places the Army had installed more than one ground rod by running one section of wire from the panel to the rod, then a DIFFERENT section of wire from the first rod to the second rod. He also reported that I need to pull the rods up a little, as the connection is not accessible.
He is older and more experienced than me (maybe not saying much as I am 29) but I am not ready to say I am wrong yet. Any comments, especially code references? Can I run more than one GEC to a ground bar? Can I have a splice in rods in series? How do I get 8 ft of rod in contact with soil (250.53G) and have some of it out of the ground?
Thanks!