E electriciansd Member Jun 7, 2011 #1 Is it allowed by the NEC to use weatherproof bell boxes inside the elevator where grain is being handled
Is it allowed by the NEC to use weatherproof bell boxes inside the elevator where grain is being handled
kwired Electron manager Location NE Nebraska Occupation EC Jun 7, 2011 #2 Is it a Class 2 Division 1 location? Likely yes. Have you ever seen a bell box rated for hazardous locations?
Is it a Class 2 Division 1 location? Likely yes. Have you ever seen a bell box rated for hazardous locations?
cowboyjwc Moderator Staff member Location Simi Valley, CA Jun 7, 2011 #3 I would say that it's not allowed.
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Jun 7, 2011 #4 Possibly for nonincendive wiring.
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Jun 7, 2011 #5 What is in the bell box?
ptonsparky Tom Location NE (9.06 miles @5.9 Degrees from Winged Horses) Occupation EC - retired Jun 8, 2011 #6 The bell box would be no worse or better than the typical conduit body that is allowed. How is it being used?
The bell box would be no worse or better than the typical conduit body that is allowed. How is it being used?
E electriciansd Member Jun 8, 2011 #7 I belive that the correct answer after further research is yes bell boxes are permitted for all wiring as long as they do not contain taps joints or terminal connections. Bell boxes meet the standard set forth in 502.10(A)(4)
I belive that the correct answer after further research is yes bell boxes are permitted for all wiring as long as they do not contain taps joints or terminal connections. Bell boxes meet the standard set forth in 502.10(A)(4)