GRC all the way?

Status
Not open for further replies.

laketime

Senior Member
I am doing a commercial project bid and the service will be parallel 3" or 4" to an overhead service feed. The poco needs grc to attach to. My question is, that if I have to go up 20' to the weather head can the first 10' out of the meter socket be emt or does it need to be grc the whole way?
 

WirenutNH

Member
Location
NH
I belive that if it is either a mast or syphon service poco requires it to be all RMC. I would check to see if poco has a guide book
 

iwire

Moderator
Staff member
Location
Massachusetts
Many power companies will require the top stick to be a full 10' that means the cut section ends up at the meter base, you will either have to thread the three inch or buy a 3" RMC compression connector.
 