what's the theory on installing a ground rod at a sub panel with three wire service? leave neutral and ground bars connected?
It was more like lack of theory or understanding or the definition of a grounded and grounding conductor.
Was allowed years ago but no longer for new installs.
As for existing sub-panel, yes keep ground bar/neutral bar tied together.
so on existing sub panels with a three wire feed, driving a ground rod and keeping the neutral bar and grd bar connected will be safe and better than not having the grd rod there at sub panel at all?
We drive ground rods because we have always driven ground rods and that is the reason we will keep driving ground rods. I don't think there is a huge gain in safety having them.
What is most important is to keep a low impedance equipment ground path back to the breaker so that it will trip on a ground fault. That usually means keeping the neutral bonded at the sub panel for an existing three wire feed. We are talking about a sub panel in a separate structure, right?