Scott: For a receptacle it depends on the type of metal box and receptacle.
1. A bonding jumper is not required for self grounding recepetacle in a metal box, or mud ring
2. A bonding jumper is not required for a surface mount metal box (bell box) if direct metal to metal contact is made between the yoke and the box (remove the fiber washers)
3. For a raised cover a grounding jumper is required.
The ground fault return path has to be maintained between the receptacle and the box. For example if a self grounding receptacle was replaced with a non self grounding recpetacle than the ground fault return path can not be assured. See Section 250.146