Greenfield in lieu of Expansion Coupling

Always4

Member
Location
Philadelphia
Occupation
Electrician
I haven’t specifically found anything in NEC that says you can’t but is there anything against using a section of greenfield instead of expansion fittings? It’s not a matter of being cheap was quoted 5-6 week lead times on Bridgeport EC-400.

This question applies to conduits carrying telecom and also conduits with branch circuits.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I see no problem as long as you use the proper transition fittings.

I wouldn't depend on them for equipment grounding continuity.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I actually preferred this method over expansion fittings.
 

Always4

Member
Location
Philadelphia
Occupation
Electrician
I see no problem as long as you use the proper transition fittings.

I wouldn't depend on them for equipment grounding continuity.
When you say proper transition fitting I’m assuming you mean something like a Bridgeport 290-XS? Instead of a 4” compression connector- 4” Rigid Coupling- and a 4” Greenfield connector on each side?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
When you say proper transition fitting I’m assuming you mean something like a Bridgeport 290-XS? Instead of a 4” compression connector- 4” Rigid Coupling- and a 4” Greenfield connector on each side?
Exactamundo.