I just had an inspector cite us for the use of greenfield whips for connecting 6" cans in a remodeled wine cellar. Each whip was much less than six feet and were used because piping would of been very difficult. His issue was the "daisy chaining". We used a grounded conductor in each one but doesnt matter. We have to redo whole ceiling. General contractor is not happy. Where is this in the code? This job is in suburban Chicago operating from NEC2011
 

kwired

Electron manager
Location
NE Nebraska
I just had an inspector cite us for the use of greenfield whips for connecting 6" cans in a remodeled wine cellar. Each whip was much less than six feet and were used because piping would of been very difficult. His issue was the "daisy chaining". We used a grounded conductor in each one but doesnt matter. We have to redo whole ceiling. General contractor is not happy. Where is this in the code? This job is in suburban Chicago operating from NEC2011
What size FMC and what size of conductors did you use?

3/8 flex can be used in up to 6 foot lengths for "fixture taps", but such installation would have to have an individual drop from junction box(es) to each luminaire and not run from luminaire to luminaire.

You can run 1/2 inch or larger FMC with properly protected conductors 14 AWG or larger in the manner you mentioned - if you also pull an EGC in the raceway.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
1/2" flex with full-sized (for the circuit) conductors is equivalent to 1/2" EMT with the same sized conductors, as long as you secure according to the rules,and there is no problem daisy-chaining with it. I believe the forum will agree that the inspector is wrong, and you should definitely appeal/challenge his decision.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I agree with Larry however, I see you're in Chicago and they have their own code, might this be where the inspector is coming from?

Roger
 

forcebjj

Member
Location
Chicago Illinois
greenfield whips

thank you for your responses, the whips were in 3/8. however he made no mention of size which we would of happily replace. He simply said no daisy chaining in flex all hard pipe. It is a mute issue the whole ceiling is being dropped as we speak. the authority having juristiction has spoken. The client is not happy now the ceiling will be 10" lower:rant::rant::rant:
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
Many years ago we had an EC from Chicago post pictures of his residential rough-ins, all with EMT. The only place he used Greenfield was for the porch light outside the front door because it was to be a cut-in box. I remember a room with recessed lighting, I don't think he had a problem. :happyno: