Greenhouse Wiring

Status
Not open for further replies.

Jim Decker

New member
We're installing a new detached greenhouse. We want to bring both normal and emergency power from the nearby existing building. Is this allowed by the NEC.
 
Yes. Reference 225.30(A). But I think it is more likely to be appropriate to call this an "Optional Standby" system, rather than "emergency."

Welcome to the forum.
 
I agree with Charlie and will add that if you actually have 'emergency' circuits they will have to be kept separate. If the circuits are as Charlie said 'optional standby' then they can be mixed with the normal wiring.
 