hello all, whats the code for the gauge of wire to hold lay-in fixtures independent of the ceiling ? Im pretty sure its a building code .... any help would be great ....
stickboy1375 said:Your right, it is a building code.
cowboyjwc said:Light fixtures weighing less than 10 pounds shall have one, No. 12 gage hanger wire.
Light fixtures weighing more than 10 pounds but less than 56 pounds shall have two No. 12 gage hanger wires.
Lighting fixtures weighing 56 pounds or more shall be supported directly from the structure above by approved hangers. Supplementary hangers are not required.
Pendant-hung fixtures shall be supported directly from the structure above using No. 9 gage wire or an approved alternated support without using the ceiling suspension system for direct support.
This is out of the CISCA standards for seismic zones 3 & 4.
benaround said:When using grid wires for lay in fixtures, is it considered " independent " of
the grid and 410.16(C) 2005 does not apply ? I say this because the OP used
the word " independent" , IMO, these fixtures still need to be fastened to the
grid by bolts, screws, or rivits.
raider1 said:The requirements in the CISCA guide require both attachment to the grid system as well as the independant ceiling grid wires.
Chris