rcwilson
Senior Member
- Location
- Redmond, WA
We have a project on an industrial site with an existing sump and grinder pump that pumps the flow from a single toilet and wash basin up to the main sewer system. The sump and all components in it (level switches) are suitable for Class 1 Div 2. The pump motor sits on top of the sump with the pump down below. The existing installation was considered non-classified. The sump is flush with the floor in a utility substation service building that houses transformer oil processing equipment, but the entire building is considered non-classified. (Transformer oil is not considered a flammable or explosive liquid, similar to diesel fuel. No oil drain goes to this sump, unless someone dumps oil in the toilet).
As part of a new installation we changed the pump to a different voltage, using a motor listed for Class 1 Div 2.
Our PE stamped the drawing showing the area as non-classified, quoting NFPA 820, Table 4.2 "Collection Systems", Line 9, which shows a Not Normally Ventilated (NNV) pumping unit in an enclosed area serving one but not more than five dwellings is unclassified. The table lists grinder pumps specifically and the description fit the installation. We could not locate another NFPA reference that discussed classifying grinder pumps.
The AHJ has objected to the area classification because Table 4.2 Line 9 is for "Individual Residential Pumping Units,...(e.g., grinder pumps...)" and this is an industrial facility.
All the other categories in NFPA 820, Table 4.2 are for larger municipal sewer systems, pumping stations and mixed residential and industrial wastewater where possibility of flammable liquids is greater than a single toilet. All categories recommend the enclosed space (building) above the larger sumps as either Class 1 Div 1 or 2. The recommendation from the AHJ is to classify the entire existing building. That is not practical or necessary.
Question -Is there any other reference we could site to back up our engineering judgment that this single toilet grinder pump installation does not require classification of the entire existing building?
As part of a new installation we changed the pump to a different voltage, using a motor listed for Class 1 Div 2.
Our PE stamped the drawing showing the area as non-classified, quoting NFPA 820, Table 4.2 "Collection Systems", Line 9, which shows a Not Normally Ventilated (NNV) pumping unit in an enclosed area serving one but not more than five dwellings is unclassified. The table lists grinder pumps specifically and the description fit the installation. We could not locate another NFPA reference that discussed classifying grinder pumps.
The AHJ has objected to the area classification because Table 4.2 Line 9 is for "Individual Residential Pumping Units,...(e.g., grinder pumps...)" and this is an industrial facility.
All the other categories in NFPA 820, Table 4.2 are for larger municipal sewer systems, pumping stations and mixed residential and industrial wastewater where possibility of flammable liquids is greater than a single toilet. All categories recommend the enclosed space (building) above the larger sumps as either Class 1 Div 1 or 2. The recommendation from the AHJ is to classify the entire existing building. That is not practical or necessary.
Question -Is there any other reference we could site to back up our engineering judgment that this single toilet grinder pump installation does not require classification of the entire existing building?