gronded conductor

Status
Not open for further replies.

domnic

Senior Member
Occupation
Electrical Contractor
On a corner grounded three phase delta service the grounded conductor is marked white at the meter base and in the panel. once a three phase branch circuit leaves the panel must you mark the grounded conductor in the branch circuit white ?
 
On a corner grounded three phase delta service the grounded conductor is marked white at the meter base and in the panel. once a three phase branch circuit leaves the panel must you mark the grounded conductor in the branch circuit white ?

Of course. Why wouldn't you?
 
On a corner grounded three phase delta service the grounded conductor is marked white at the meter base and in the panel. once a three phase branch circuit leaves the panel must you mark the grounded conductor in the branch circuit white ?

it is still the grounded conductor.
 
While the code requires that grounded conductor to be identified just like any other grounded conductor, in the 20-30 grounded phase systems that I have seen, I have never seen the grounded conductor so identified.
 