Re: Groud Rod Testing
Don I am not familiar with the Amprobe model DGC-1000, I assume it is a clamp-on type like my AEMC. If that assumption is correct, if used properly the meter will always read higher than the actual impedance. The reason is it reads the UUT in series with all the other parallel sources.
For example lets assume we have four rods buried in the ground and connected together. Lets also assume each rod has an impedance of 100-ohms. If we clamped any one rod we would measure the one rod of 100 ohms plus the series impedance of the 3-rods in parallel and our meter would read 133-ohms.
Now the kicker is the 4-rod system I just described is really 25 ohm system because 4 rods of 100 ohms in parallel is 25 ohms. However lets take the example one step further. Lets say we have the same 4-rod system in place connected to the AC service properly and we clamp the service grounded conductor. Here are the assumptions:
1. the 4-rod system as a whole is the same and a value of 25-ohms (4-rods @ 100-ohms each).
2. The service neutral is a MGN system and has an earth impedance of say 2-ohms.
In this example the meter would read 27-ohms. Not bad, close enough for government work!
To be really accurate requires us to disconnect the service grounded conductor and use a 3-point fall of potential test. Howevwer it is still a calculated measurement because it has to be done from several locations, none of which will measure the same, and has to be averaged out.