zemingduan
- Philadelphia,PA
- Electrical Designer
We have (3) outdoor single phase 4160V - 480V transformers connected in delta and form the transformer bank. The (3) transformers are not utility transformer. They have another onsite transformer that step down from 13.2KV utility service to 4.16KV. I guess they are previously used for manufacture factory. The electrician propose to reuse the transformer bank to supply a 1200A 480V 3ph 3w disconnect located inside the building. And they can use 480V delta - 480/277V wye transformer in the future as needed.
I think we should ground and bond the ungrounded separately derived system per 250.30(B). We will need to make the grounding electrode connection to connect the transformers metal enclosures to the building grounding electrode system at the transformer bank for outdoor source per 250.30(C). We will need to have supply-side bonding jumper to connect the transformers metal enclosures to the 1200A disconnect inside the building. Then done! Please correct me if I am wrong.
But how are the grounding electrode connection and supply-bonding jumper connections made at the 3-transformers bank in reality? I need a grounding & bonding detail showing these connection. I only know how it is done for a transformer that has all three phases windings in one enclosure. Please help. Thanks!