ground amps

Status
Not open for further replies.

Brandon Loyd

Senior Member
I am told that up to 5 amps measured on ground wires is acceptable by either B
NETA or code due to phantom induction amps. Can anyone confirm this?
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
Give a detailed description of your ground wires.

If I find 5 amps of current flow on the equipment ground of a 15 amp branch circuit, absolutely not.

5 amps of current on a water pipe bond to a neighberhood metallic water pipe may just cause me to ask questions then, depending on the answers, go home and sleep well.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I found between 2 and 3 amps on my water pipe the various times that I've checked it. I would consider that to be normal.
 

Brandon Loyd

Senior Member
In this case, we check the ground wires in the main electrical room where they all come together at a ground hub mounted on the wall. See attached picture.
 

Attachments

  • DSCN5468.jpg
    DSCN5468.jpg
    142.5 KB · Views: 0

brian john

Senior Member
Location
Leesburg, VA
Did you measure at the water connection?

Was this on two conductors or more?

This could be a variety of issues, could be circulating current a result down stream ground connections or leakage current from loads.

How big is the facility?

That I know there are no standards for allowable current on the ground.

I would recommend an outage and an insulation resistance test on the neutrals with the neutral disconnect linked removed. If shorted isolate the feeders then the branch circuits.
 