I am currently at a facility that provides electrical utility to about 250 customers. Most Customers are on a 3 phase 4 wire wye system. This infrastructure was built and designed back in 1969. There are about 11 substations at this facility stepping voltage down from 4160 to208/120, 3 phase. All the substations XFMRs neutral lines has been bonded tobuilding steel and a ground ring, all existing meter bases has the neutrallanded on the neutral bar in the meter base which is bonded to the metal enclosure of the meter base. A ground wire is also landed on the ground terminal of the meter base. A new inspector has started inspecting all new services at this facility. He raised a flag of bonding the ground and neutral at the meter base and XFMR at the substation. They did not want to void the UL listing of the meter base by floating the neutral in the meter base. His answer was to not ground the meter base run Plastic PVC in and out of the meter base to keep it isolated from building steel and the main panel. The meter bases do not come with any kind of isolated neutral bar or kit. Now you have a meter base that is not bonded to building steel. Is this the best solution? Could the way it has been for 40 yrs. stay through a grandfather act somehow? The infrastructure has had its share of faults in its time and worked. I understand where the inspector is coming from but I want to make sure his solution is the best answer?
Thanks for your help