xguard
Senior Member
- Location
- Baton Rouge, LA
There is no code issue with the EGC connections in the photo unless they haven't properly cleaned the metal surface.
So what about using what the panel lists for grounding lugs and bars? Is bolting your own individual lug in a panel code compliant when its not listed in the panel instructions?
and it appears in the picture, he had to make his own bolt hole pattern for those lugs.
If the instructions don't say you can't do it, I do think it's a clear violation.
In the 2008 NEC, 408.40 states "...Where the panelboard is used with nonmetallic raceway or cable or where separate equipment grounding conductors are provided, a terminal bar for the equipment grounding conductors shall be secured inside the cabinet. ..." This does not indicate that individual lugs are acceptable for multiple equipment grounds. As a former NYC inspector, this would have been grounds for a violation, as well as the self tapping screws attaching the lugs. A listed terminal bar bolted or attached with threaded machine screws would have been required to correct this.
In the 2008 NEC, 408.40 states "...
I can't tell from the blurry photo what types of screws are being used, it's also hard to tell but that may not even be a panelboard in the photo.
Even still it has instruction sticker inside that shows what grounding lugs to use.It's a fusible switch.
Sheet metal screws is an issue if relying on them for bonding. So are machine screws if not engaged at least two threads or if a nut is installed on back side.In the 2008 NEC, 408.40 states "...Where the panelboard is used with nonmetallic raceway or cable or where separate equipment grounding conductors are provided, a terminal bar for the equipment grounding conductors shall be secured inside the cabinet. ..." This does not indicate that individual lugs are acceptable for multiple equipment grounds. As a former NYC inspector, this would have been grounds for a violation, as well as the self tapping screws attaching the lugs. A listed terminal bar bolted or attached with threaded machine screws would have been required to correct this.
Use of the mentioned bars or lugs in the positions designated for them is simple for the reason the combination of what you have was listed/tested per those instructions. You shouldn't need to scrape any paint, add additional hardware, etc. to use those combinations.Even still it has instruction sticker inside that shows what grounding lugs to use.