From secondary of utility xfmr, we tap off (2) disconnects, each disconnect will then feed two different buildings:

1. Does above two disconnect need to follow rule of table 450.3(B) note 2?

2. Do we require to bond grounding system of two buildings together?


Thanks!
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Article 450 does not apply to a utility's transformer.

The secondary conductors of a utility transformer are service conductors.