It has been very long time that I am dealing with this problem and I would like to know your opinions on this a long with your justification.
1- Do we need to bond electrical ground system and instrument ground system (clean ground)?
To explain that in industrial plant you will see different ground system i.e. high voltage ground system, low voltage ground system, clean ground grid....
NEC requires to bond all the ground grids. But the problem is when you connect them together you create a loop between two grid that they are not definitely at the same voltage level and that creates ground loop current that sometimes is significant (I have been reported to 10 A in some cases)
BUT IEC has different rules (i.e. direct connection, using LA and isolated). for Instant IEC uses a surge suppressor or a lighting arrester to bond clean ground to electrical ground grid or in some cases it is a requirement that leave high voltage and low voltage ground grid isolated i.e. for transformers.
What do you think? Which one is correct?
2- Equipment grounding
Both NEC and IEC requires to ground equipment and both requires to have multiple ground location when the equipment is large for safety reasons. But when we connect an equipment to ground in two location you actually create a ground loop and consequently ground current.
What is your idea about that?
1- Do we need to bond electrical ground system and instrument ground system (clean ground)?
To explain that in industrial plant you will see different ground system i.e. high voltage ground system, low voltage ground system, clean ground grid....
NEC requires to bond all the ground grids. But the problem is when you connect them together you create a loop between two grid that they are not definitely at the same voltage level and that creates ground loop current that sometimes is significant (I have been reported to 10 A in some cases)
BUT IEC has different rules (i.e. direct connection, using LA and isolated). for Instant IEC uses a surge suppressor or a lighting arrester to bond clean ground to electrical ground grid or in some cases it is a requirement that leave high voltage and low voltage ground grid isolated i.e. for transformers.
What do you think? Which one is correct?
2- Equipment grounding
Both NEC and IEC requires to ground equipment and both requires to have multiple ground location when the equipment is large for safety reasons. But when we connect an equipment to ground in two location you actually create a ground loop and consequently ground current.
What is your idea about that?