DrSparks
The Everlasting Know-it-all!
- Madison, WI, USA
- Master Electrician and General Contractor
So normally I use a meter bank with integral main breakers for a multi-family residence. however in this case I have a two family dwelling and the owner provided a Milbank twin meter socket with no disconnects. he also provided to main breaker panels 100 amp. normally I run the grounding electrode conductors for the water main and ground rods to the meter socket enclosure where it is bonded to the neutral bus bar. in this case I will need to find the grounding electrode conductors to the neutral bar in each main breaker panel. my question is can I run one grounding electrode conductor to the first panel from the water main and the ground rods that being number 4 gauge copperand then jump from the first panel to the second panel with 4 gauge copper. or will I need to run a separate grounding electrode conductor from each panel to the ground rods in the water main bus having two separate conductors and two sets of clamps on each ground rod and the water main.
